  1. The complaint was ac system inop. I could see the compressor engagefor a split second. I found the system wave very overcharged. I pulled 6 pounds out and the system calls for 3 pounds. I put three pounds back in after a 10 minute vacuum with a leak test for another 10 minutes. The low side would drop to 5 pounds and shut off the compressor. The high side was around 250-275 and engaged the fan at 300. I thought the expansion valve was sticking and not allowing refrigerant to pass as should. The dryer looked old so I replaced it at the same time as a service. Now the low side is a little higher “10-15 psi” but still to low. The temp out off the vents read 58-60 degrees. 

  2. 2 hours ago, 1965 said:

    Really I know enough to get by, I know everything needs to be clean, pull a good 30 minute vacuum. Would think low side should be around 25 to 30 & high from 250 to 280 range. Also thought engine fan was supposed to run any time air conditioner compressor was on.

    The fan will engage when the ac high pressure switch closes for condenser cooling. When pressure is below the 300 the fan will not be on. 

  3. The blower has an issue cutting out and the relay getting very hot. I traced the issue to the selector switch on the hvac panel. But I have removed the blower and cleaned and tested the motor. The evap has a skin of ice on one side looking at it with the panel off. It doesn’t freeze up solid but it does form on the copper tubes on the side of it. 

×
×